Monarch has been inconsistent with respect to high-leg (which is akin to maufactured leg in an RPC system).
If you trace the wiring around the main contactor you will find that one end of the circuit which includes the main contactor's coil goes to one input terminal. We'll call that A for now. And if you continue that trace you will find that the circuit goes through the coil and also the overloads. We'll call that C for now.
You want the non-high legs to go to A and C. Obviously the high-leg goes to B.
This is really more of an issue in an RPC system where the B leg is subject to periodic droops as loads are applied.
The presence of a coolant pump is significant on later machines as these, too, utilize contactors and overloads with the same issues.
It was the M-G machines which had a main contactor for protection of the M-G itself, but employed no protection for the coolant pump (it was controlled through a simple drum switch).