240v RPC - 240v 3P XFMR 480v - 480v XFMR 240v - 240v Compressor
Original thread starter here ...
First thank you for the responses...
Ive learned in my research that a 3 phase transformer used on single phase will not perform as expected (lower output voltage) due to the reduced magnetic flux in the common core, from the lack of the 3rd phase.
Not so. Most are wound on common 'iron', so they no longer act as three independent 1-P would do. Furthermore, the KVA ratings do not remain the same when only a portion is utilized in that manner. Serious upsizing would be needed.
A proper 1-P step-up is needed instead. High-voltage idler, then 3-P step-down better perhaps than 1-P step down ahead of a lower-voltage idler.
Much better to convert to 3-P with an RPC placed at the head end, use 3-P step up for transmission, then 3-P step down at the load-end.
The two 3-P transformers used as-designed, plus the impedance of the wire, can then actually assist with smoothing and stabilizing the generated leg.
Add a smaller supplementary idler, load end, caps for mid-usage range, and it is about as good as RPC'ed power gets.
But only 75 feet?
Probably far less costly to:
A) JF live with some drop,
B) Place the compressor at the head end, run 75' of large-bore air tubing. Average shop can easily run that footage in addition, anyway
C) pull larger wire, or
D) pull a second circuit, use two RPC's, dedicate only one to the compressor, split the other loads accordingly.
Transformers plus the freight for the heavy buggers are not as cheap as any of those four alternatives.
Monarchist,
Thanks for the fresh eyes on this. I like the idea of the 2 XMFR idea. It may possibly allow me to work with what I have on hand. My original thoughts of running the compressor on 480v had me redoing all the breakers, magnetic contact heaters, capacitors and motor winding configurations.
With only running 480v on the longest wire run and XMFR back to 240v at the compressor I get accomplished my main goal.
Heres the "possibly" part .. my second transformer
I dont know if this will work for either of my transformers. I believe it to be large enough (those are 3 - 400A fuses left of the 7up can, on the input to the transformer) but my knowledge of transformers is still limited. This XMFR pictured is from a Robicon VFD and I only have there part number to go by. Looking it over I notice the 3rd winding from the left is slight smaller and without all the taps the other cores have.
Any help in identifying the type of XMFR I have?
Also any links to some good reading on transformer theory and design would be much appreciated.
I wouldn't think voltage drop on 75' of #2 copper wire would be very significant with that size load... probably <1%? Is your voltage too low at the compressor?
What you propose sounds like a lot of expense and effort for minimal return.
Impractical,
Your correct a lot of effort but I am also trying to use what I have on hand.
I am also exploring my power factor correction/voltage balance in an effort to minimize voltage drop. In the process of looking into this transformer idea and the knowledge gained along the way I learned while I thought my voltage balance was close enough, maybe its not.
Very little voltage imbalance in 3 phase motors can equal a large current difference. I have only recently got a clamp meter capable of measuring the current draw on the 3 phase legs. Measuring the actual current on the 3 phase legs on the compressor motor with it loaded will be my task before getting into wiring any transformers.
How much money to keep a 150kva xformer lit, versus buying bigger wire ?
And is the 150kva xformer free ?
Digger doug,
Also good points .. I'm not sure what the losses are in a 150kva transformer but I know they are more than in a 15kva transformer. Again my transformer knowledge is lacking. I do know copper wire larger than #2 THHN to go the 75' would have cost me more than what I spent on the 150kva XFMR, although not by much. In hind site the 150kva was a "more money than brains moment" where I took advantage of a opportunity thinking I could always sell it if I didnt use it.