For the veterans out there, what is a good box I can buy for my vfd? It will be inside and mounted in on the wall. Possibly inside the garage (worst case).
A good box is one that fits the spec. Read your manual page 2-8.
http://www.hitachi-america.us/supportingdocs/forbus/inverters/Support/WJ200_Instruction_NT325X.pdf
You are going to need a box at least 8.19in wide, 12.9in tall, 6.7in deep. Cutting out ventilation holes for air has to be done.
Hammond.
Industrial Enclosures - Hammond Mfg.
Hoffman is another brand I use. If you are feeling rich then look at the prices on the stainless steel ones.
Hammond.
We do but the ones I've dealt with I would rather walk on glass. I'm the little guy that they don't care about.I don't like it because it does not have a hinged door. I think it's a ripoff. Don't you have any surplus electrical supply outlets where you are? At this place I have to decide which of the items I don't want.
This one has a hinge
New SCE Electric Enclosure SCE 14128ELJ NEMA 4 12 13 | eBay
Hammond.
That is not true. As long as the enclosure is big enough, and otherwise meets Hitachi's specs, it can be fully sealed. The heat simply transfers through the area of the walls. The walls simply have to be big enough, hence Hitachi's specified standoff distances between the bottom, sides, and top of the drive and the walls.
Sounds like a good idea for a large hand warmer in the winter time.
I like the continuous hinge door types. Unfortunately if the enclosure I want to use has door clamps I grind off the tack welds and remove the clamps. Then I install a door latch. I also don't care (too much) if the enclosure has a few holes. I get the right gauge steel and turn coin plugs on my lathe and tack weld the coins in the holes. When I am finished the enclosure looks like new. Used ones I have bought are like $30, $45.
I remember reading something about switching loss, the higher the frequency the more heat generated. Yeah, that's it. It's all coming back to me now, the times I worked in chilled raised floor mainframe computer rooms with fans in every compartment. The VFD will last longer with air flow.It IS the reason for the large enclosure. Heat is transferred by radiation AND convention to the inside. Same again transfers it from warm box to ambient air outside. No ingress for dirt or splash required.
Check the specs.
Typical VFD or DC Drive only wastes about 5% of the total itself.
Rest of the heat is shed at the working load, not always a motor.
Bill
Just for a lark... I counted the holes on two brand-new Eaton/Cutler-Hammer 3-P load centers recently acquired. 161 possibile holes, each, four sides and back if the multi-diameter knock-outs are counted one for each size.
But ... they ain't meant to be a submarine pressure-hull, Ron.
Common snap-in plugs, ELSE the bolted-in ones - whichever suits - and yer back to NEMA spec.
Lathe-turn & tack-weld? You have waaaay too much time on yer hands.
Bill
No, I just hand out first rate information and do first class work.
Notice