Mark L Tucker
- Jan 30, 2018
Hi
I have had a PhaseQuest OMPQ-50 RPC wired in my shop and for the last 6 months it has been doing its job great but 2 weeks ago it was idling while I was setting up the next job I heard a crackling noise from inside the panel, then the idler motor bogged down and within a couple of seconds it blew the end off of one of the start capacitors. I have has an electrician out 2 times now and each time we think its right it seems to overload the start capacitors.
I'll list everything that's happened and been done so far;
1. start capacitor blew and I noticed a wire on the run capacitors was completely burnt out and not making a connection. Changed the start capacitor, fixed any damaged wires and re-crimped any loose connection
2. started the RPC, the idler motor was slower to spin up and before it got up to speed it blew the start capacitors again. At this point I figured it would be a god time to call the electrician in.
3. the electrician checked the unit and found that I had 7 blown start capacitors and the contactor was welded shut. He checked the run capacitors and they all tested within their operating range. He also checked and changed out some wiring and tested for resistance between the phases on the idler motor.
4. this time when we started the unit the idler motor spun as it should have but within 2 seconds it
let out a bang and lit up the inside of the panel (Im sure where the start capacitors are). We opened the cover and found that 3 of the start capacitors had been weakened and were now testing at the low end of their rage.
5. at this point the electrician figured it must be the starter relay and ordered a new one up. He fitted that and just to be sure there wasn't an issue after the phase converter we disconnected the lines going to the transformer. When we started it the same happened where within 2 seconds it let out a bang and a flash of light.
At this point the electrician is also scratching his head and so I was hoping someone on here may be able to offer some guidance.
Could the flash and bang have come from the start capacitors discharging as there was zero load with the transformer being disconnected?
Although I know the electrician was very careful is it possible that some wires have been crossed?
I should also say that when it flashes and bangs I immediately shut it down and so I don't know if it would successfully switch on to run capacitors and continue to run.
Any advice would be greatly appreciated
Thanks in advance
Mark
Thanks in advance
Mark