Hi folks,
I've been doing a lot of reading on the web and around here, and I think "I have it all figured out", but I'd really appreciate a second or third, or ... opinion. My goal is to determine I'm okay to run an induction heater from an RPC. The heater is an induction heater which has a max rating of 40A @ 240V 3-phase.
My shop: 100A 240V sub panel from my house, which has 200A. To my property I also have separate 200A service for our hvac system, so 400A total from the road.
Consulting with an RPC company, they recommend a 30HP machine based on the suggestion that you want to run at <60% capacity for an inductive load. A 30HP RPC is about 49A.
The 30hp RPC has a soft-start feature, which they say will require 1x the max current of the idler to start, which is 65-75 single phase amps.
Idle amps for the RPC are 7A single phase.
My analysis:
RPC: The soft start coming in at 75 amps will be okay to get the RPC running (based on my similar experience with the 5hp, single phase compressor, which starts fine with no flickering).
Induction heater: Turned up to 100%, this will draw 40A three-phase, which is about 70A single phase + idler or close to 80A total.
My naive conclusion is that we are okay(as long as the compressor doesn't come on. )
The induction heater would probably be running at a 30% duty cycle at 100%, with it most often running in the 50-60%, maybe. I would have to manage what is running at the same time, but overall I believe I fit within my bounds.
So my question is - is this all there is to it, or am I missing something? I am going to blow up transformers or invest in machines I can't suitably use?
(Note that I did call the power company about this, and they said something like "we don't make recommendations of that sort", so it seems like they aren't too worried).
I would appreciate any input on this.
Don
My analysis:
Don