The curves are available from the manufacturers, they are nearly always on the website. All the product specs generally are.
But fuses differ a lot. There are regular time delay, and there are "current limiting" types. The current limiting ones will interrrupt the current without exceeding a certain amount of peak current, with voltage and available current from the power source up to the max rating of the fuse. Non-current limiting may "let through" an unspecified peak current.
The absolute minimum current depends on how long you wait..... Some fuses are rated to carry their rating forever, to carry 135% of the rating for at least 4 hours, and to open at 200% in a specified short time. Others have different times and current ratings, often still at 135% and 200% of marked rating.
The current also depends on ambient temperature. A fuse works by melting, and the hotter it is to start with, the less energy (and current) it takes to melt it. So it's rated for more current when very cold, and less current if in a rather hot area. Temperature affects both ultimate current, and also time to melt (open).
Just because the fuse is rated at "X" amperes does not mean it will necessarily open in a precise time, or ever, at a slightly higher current. Normally it takes a considerably higher current to melt the fuse.
US and european fuses also differ, US beng rated on carry current, and european on opening current.
Here is a LOT of info on fuses... more than you want, probably.....
http://www.littelfuse.com/~/media/e.../littelfuse_fuseology_selection_guide.pdf.pdf