Botje
- Mar 26, 2012
- The Netherlands
Hi guys,
Question. I've been trying to diagnose a problem with the VFD of my Okuma LS lathe.
What happened. Didn't use the lathe for a month, it was simply too cold in the shed. Went to use it again, motor not running, only jerking and banging the gears of the headstock. Within short time overcurrent fault triggered.
Tried a spare (old) 4 KW motor, same effect, with original parameters and with current etc set for the other motor.
Checked IGBT's and diodes for continuity, all checked out fine with my Fluke meter. Power supply good too, all 3 phases 400V.
Checked the parameters. Some seemed off. Changed them back to factory setting, motor runs good! Checked motor resistance good. Motor phases same voltage. Maybe slightly uneven but hardly noticeable.
Now the strange things. Works fine on Vector field control mode. On VF mode the lights start to dim/flicker at high rpm and some high pitched humming noise is heard from the VFD.
And, the DC bus is only 570 Volt and decreasing with higher motor rpm. Normally a 3 phase 400V grid has a DC peak value of 690V. DC bus voltage just doesnt get over 570V.
Maybe bad filter cap?
The issue here is that this VFD has a form factor that works good with the original cabinet. So not easy to just buy the cheapest VFD on my local Craigslist and use that one.
Mains swith (4 pole) - circuit breaker - relay - VFD.
Thanks in advance!
- Original 1973 7,5 Kw motor, over here running on 400V 3 Phase supply (motor in delta)
- VFD replaced old star/delta starter
- VFD is a SEW Eurodrive Movitrac unit rated for 7,5kw worst case.
- VFD fitted in original cabinet with ventilation.
- Most wiring replaced.
Thanks in advance!