david n
- Apr 13, 2007
- Pillager, MN
I need to drop my voltage from 240(more like 248) to 220. 3ph open delta. 24 kVa. I really don't know much about them. Where to start? TIA
One of the issues I see is that new equipment as in the case of Southwestern Industries 2OP is spec'd out at 220 volts 60 Hz. That gets to be a problem in that with the nominal voltages around 240, that with delivery tolerance from the power company, the supply voltage could easily be outside the allowable range for the equipment. This happened with my associate, the voltage out of the RPC was 250. The installation tech suggested that the voltage be dropped. Other than a buck/boost, the power company would have to lower the voltage.
Tom
Tom
Exactly my situation................
2.4.16
Transformer
The TRAK 2OP mill must be ordered for 200 to 240 or 400 to 480 volts. A transformer outputs
115 and 24 volts. During the installation of the machine, the wires to the transformer may need
to be moved to adjust the output voltage. From the factory the wires on the transformer will be
place on the 220 or 440 volt tap and 115 volt tap on the output side. It should be noted that the
transformer is physically different for 220 volt machines versus 440 volt machines.
Warning
The input voltage to the machine should not exceed 240 or 480 volts. The spindle
inverter is not rated for voltages higher than this. If the shop has voltages that
exceed these numbers, they will need a step down transformer to lower the voltage.
Voltages higher than this may void your warranty
Similar to what Jraef said, it would be helpful to know what the application and equipment specification is, to better help you select the right thing to use for the application. Like if this for a CNC that is calling for 220v, it's likely that the design voltage is more like 200 to 208V as the ideal voltage, depends on the particular machine and builder. Best to be sure before you start ordering things, electrical items are non returnable once connected.
The Acme Transformer catalog has a good deal of info in their buck boost section, to educate yourself with. Find a copy here, can be downloaded with the button on the bottom of the page.
ACM_CAT_007_0913
For the info you gave, 248V to 220V 24KVA, looking at the standard buck boost selection charts, closest match I find is, 250V to 227V (subtracting 23V) at 24KVA equates to a 1.5KVA 120x240V - 12/24V unit, Acme T-1-11684. Two of these units wired in open delta provides 27KVA capacity.
Your voltage of 248V - 23V = 225V net result. Is this where you want to be? Does it meet the equipment requirements?
SAF Ω
No, your power being at 248V is ALREADY consuming a portion of the 240 +5% allowable by the utility service. You don't get 248 +10% on TOP of that.Now that I think of it, machine needs 205-235V. The +/-10% allowed by the MFGR, at 235V the machine should still be OK up to 259V.............right? My power(+/-5%), 248V, would be at most 260V. I'm riding that fine edge..................
And from the manual of that unit, I'd say they used a marginal design and did NOT follow the +-10% rule. As I said, it's not a requirement, it's just what's called "conventional wisdom" for designers to follow NEMA (National Electrical Manufacturer's Association) design guidelines.
And from the manual of that unit, I'd say they used a marginal design and did NOT follow the +-10% rule. As I said, it's not a requirement, it's just what's called "conventional wisdom" for designers to follow NEMA (National Electrical Manufacturer's Association) design guidelines. These guys obviously did not, they are saying that 240V is the hard upper limit. In this country, that's tough to meet, I rarely see a 240V service that isn't a few volts high or low during a work day, even higher after hours. But it shifts the burden off onto the buyers to make sure the CNC doesn't fail. Kind of a cheapskate design philosophy if you ask me.
What are the downsides to this approach vs. full 3 coil autotransformer and/or 3 coil isolation transformer?
This surely is the lowest cost option.
15. Why isn’t a closed delta buck-boost connection recommended?
A closed delta buck-boost auto transformer connection requires
more transformer KVA than a “wye” or open delta connection
and phase shifting occurs on the output. Consequently the
closed delta connection is more expensive and electrically
inferior to other three-phase connections.
Buck Boost or open delta will pass transients and common mode noise. Full isolation with a closed delta to wye is much better at reducing transients and common mode noise. A lot of machinery vendors require a full isolation delta/wye for warranty. If it's a machine or two on a clean distribution system probably no problem with the open delta. If you have a building full of CNC equipment, the noise and common mode currents can build up and circulate causing problems with the equipment. With a 3 coil autotransformer the cost benefit is removed, then the full isolation is just as good.
From Acme Q&A
SAF, there is some mix and match nonsense in the FAQ answer..... I don't have time to pick it apart for correctness right now, but ok.
YOUR reply is spot on and correct of course.
I posted my question to try to get folks to comment on the GROUNDing differences mostly. I figured the OP did not require any more isolation for noise immunity.
The Grounding implications? ....
Secondly inverters and drives and their MOV protection don't like it either. I'm no drive expert, came here to learn about that part.
What I have gleaned so far is that generally the drives and their MOV protection is set up expecting a wye configuration for balance, and if it isn't, that can lead to problems. Some drive manuals that I have perused call for removing a jumper on the MOV connections, when a delta is used, others forbid a corner grounded delta altogether.
Notice