squeeze
- Jan 20, 2012
- Connecticut, USA
I have several 5.0 - 5.5 (16.2 amp max) hp loads on a rotary phase converter (RPC - Phasemaster MA1-B) whose nameplate states that the "largest motor" hp is 7.5, with total of 22.5hp. I have it powered (single phase) by a disconnect switch with a 40 amp two-pole breaker and 35 amp two-pole time delay fuses. Wired with 8 awg single-phase input and 10 awg 3-phase output. The machines are not run concurrently - though nothing prevents them from being run. Technically, any of these motors could be run on a 12 awg wire, but then that wire would be protected by a 35 amp time delay fuse which ... is likely not safe.
I'd like to extend the 3-phase to some smaller machines - tapping off the disconnect box with conduit and running to several outlets. The first outlet should support that 16.2 amp max load, and then the second outlet should support a much smaller motor in the 2hp range (5.6FLA at 220volts).
I'm confused about a logical approach. My gut tells me I should have a 3-phase breaker panel between the RPC and the machines with at least two 3-pole breakers. A 30 amp 3-pole breaker for the 5.5 hp with 12 maybe 10 awg, and 15 amp 3-pole breaker with 14 awg. Since a 3/4 conduit can hold up to 11/10 awg thhn, I should be ok putting the four 10 awg wires and four 14 awg wires in the same conduit for the less than 40 foot run? I'd also be ok using time-delay fuses instead (probably a 12amp and 25amp respectively)
Question
Is this a rational approach and if so, is there a small 3-phase load center type panel box (two, 3-pole circuits as described above) that people have used? Is there some sort of in-line breaker alternative (I have a space issue).
Question