The electrical setup I have in my shop is as follows.
I have a static phase converter that starts a 3hp 220v 3 phase motor ( pony motor)
I’ve wired that motor to a junction panel and connected my surface grinder with separate vacuum motor as well as my band saw to that panel.
Both machines start and run fine.
I just wired my series one Bridgeport to the same panel and when I start the Bridgeport it draws a high load and the motor is louder than expected, sort of a groaning humming sound.
Once the motor is up to speed it quiets down. It’s a 1hp induction motor and I start it with no load, slacken the V belt
The motor is a Fairbanks, I believe it’s called a pancake motor, and it’s rated at 3.8A at 220v.
Any ideas what might be wrong.
Thanks, Steve
Fear not. Your hardware is in better shape than your description OF it...
To the extent your so-called "pony motor" does NOT have any "shaft load" placed on it, it is not a "pony" motor, it is a "pilot motor" AKA Rotary Phase Converter "idler".
So far, so good.
A(ny) static converter does ZERO "conversion" of itself. All it does is kick a 3-Phase motor off "rest" in a chosen direction of rotation, then run it on one winding set as single-phase @ a tad under 1/3 wotever the nameplate HP happens to be .. "etc"..
IF/AS/WHEN reconfigured properly, a "static" convertor-not-really can ALTERNATIVELY serve as a starter ON/OFF control for a "pilot" or "Idler" motor reasonably well. .and you THEN have a "Rotary Phase Converter".
Commercial makers of 'static' converters (NOT!) usually publish the 'how to' info, and we presume you have already put that into practice.
"So far" still good... you NOW HAVE a "Rotary" Phase Converter.
Already. And they DO "convert".
So you are about 75% of the way to where you need to get to.
Page Two:
You probably don't even need attention to run/balance capacitor values to better optimize the rig AS a proper "RPC", but can't hurt to review that.
Page Three:
Your REAL problem is that Phase Converters can struggle to START certain types of load motors and ..
ta da... you NOW HAVE exactly that ... a challenging one.
An Idler larger than 3 HP is helpful, but not critical.
Try this first:
Simply turn on the
saw and let it run, no load. Optionally the grinder instead. Optionally BOTH the saw AND the grinder. The "idle" motors added "stiffen" the 3-Phase power "pool", as if it/they were a larger idler AKA "flywheel".
NOW start the BirdPort. While the other(s) run, idle.
Should come up faster and easier.
THEN shut-off the idle saw / grinder / both.
Take two aspirin, let us know how it went in the morning.
If it is a Pain In The Anatomy? Upsize the 3 HP idler.
Or furnish a 'dedicated' supplementary idler to use instead of the other load-motors on the other machines.
As said, you are "almost there" already.
"Almost" isn't good enough.
Page four:
By now we have ruled-out your "converter" as primary cause of the problem. Or easily CAN rule it out.
There still COULD be faults in the BirdPort motor.
And probably ARE.
They are NOT ordinarily so hard to start as to NEED a 3 HP idler for a 1 HP load-motor.
What you have - if decently implemented - SHOULD power-up a TWO HP BirdPort.
The power system you have is not where I would look "first".
The BirdPort's motor doesn't sound healthy.
I'll leave sorting those birdporty bits to those expert in the ports of birds.