American rotary ADX-60 high amperage on idle?

JST

Diamond
Joined
Jun 16, 2001
Location
St Louis
A standard Phase-perfect of a given rating will start any motor up to that rating.

They DO seem to have a "low cost line" that is not as heavy-duty, I forget what they call it, and it may be referenced above.
 

jim rozen

Diamond
Joined
Feb 26, 2004
Location
peekskill, NY
I am looking back over this thread and cannot see if the actual power consumption of the idler in question (the question in the title...) was ever determined with a watt-hour meter. Just curious for my own data....
 

thesjg

Plastic
Joined
Nov 4, 2021
Location
Sturgis
There are 4 second and 10 second ratings in the literature.

A 10hp phase perfect is rated for something like 150 amps 3 phase output for 3 or 4 seconds, which is what you need to start a 10hp motor (230v)

Since 2019 (I believe), rather than specifying a current for a fixed period, we include a series of overcurrent/motor starting sourcing limit charts in the Phase Perfect manual. These are a more accurate representation and show the curve of current over time a Phase Perfect can supply. These emulate a Class 10 trip curve.

PT's need large IGBT's compared to a similar sized VFD to handle the locked rotor current draw that comes with starting a motor "across-the-line". Then, we reign it in to stay inside the thermal design envelope.

You typically wouldn't need 150 A for several seconds to start a 10 horse, but you might if it has 180psi of air pushing back against a piston pump hooked up to it, or similar. That's what we design around, the tough industrial loads, such as compressors, elevators (hydraulic pumps), etc., which makes it easy to say -- yes, the 10 Horsepower PT or PTE will start your 10 horsepower motor.

current-limit-small-pt.png

Charts for other models are available in the Phase Perfect Manual in the downloads section of our website. https://www.phasetechnologies.com/support/downloads
 

JST

Diamond
Joined
Jun 16, 2001
Location
St Louis
I am looking back over this thread and cannot see if the actual power consumption of the idler in question (the question in the title...) was ever determined with a watt-hour meter. Just curious for my own data....
Not that I noticed. A wattmeter would be a little more direct.....

But it does not matter, lagging (or leading) amps will pop the breaker just as well as in-phase amp. For the breaker, all amps are the same.

To your point, I wondered if the number given for the RPC was for a unit fully power factor corrected..... although even for that it seemed low.
 

jim rozen

Diamond
Joined
Feb 26, 2004
Location
peekskill, NY
"1) is the converter in a residential bulding? If so it is probably fed through a watt-hour meter. If so then turn off all other loads and run only the rotary converter for a known time. Calculate the power used."

From post 8 in this thread. It apparently is in a buildling metered via a WH meter. It would answer the original question neatly.
 








 