My Atlantic brochures are from 1963. Moore tooling is very expensive new but used jig borers prices have fallen so much that I suspect the tooling on the used market is half way reasonable these days.
![]()
[This message has been edited by D. Thomas (edited 08-15-2004).]
Thanks for the reply. From my research I have found the same motor on eBay and it was setup for 208-220 (Red motor tag)Six wires coming out of the motor.... That's more likely a two speed motor. Only set up for one voltage. You'll either have to rewire the motor for 230 volt or find you a 230 volt motor to replace the existing one. Last option, is to wire in a step up transformer to step up your voltage from 230 volt to 460 volt.
From my research I have found the same motor on eBay and it was setup for 208-220 someone that owned it threw the years switched it to 440V. .
The polyphase motor says 208-230 volts. It's definitely a two-speed motor set up to run on 230 volts 3-phase.
I think 4GSR meant to say "dual voltage" motor, not two-speed. Motors with the connections for high and low voltages have nine wires coming out, not six. And "the same motor" doesn't mean anything, it's how the coils are wired up inside that counts. Same exact body and size and all that can be internally connected for low voltage or high voltage. Many (or most) have all the leads to connect either way. Those have nine wires. Some do not. Those have six leads and can only be connected one way.
A motor shop, if you have one, can often go inside and pull the other leads you need for low voltage operation. "If you have one" is the magic words now, US infrastructure for this kind of thing is fast disappearing.
If all else fails, you can send it to a village in yunnan where a young girl does this kind of work. Better send a brass hammer along with, she's kind of brutal
(lin guo er, youtube)
Thanks for the reply, The 3rd picture above that has the scratched out spot and 440v stamped isn't original makings someone stamped it. The motor tag with the red section is the one I found on ebay. came from the same machine as mine. If all the wires need to be the same then Don't I need to change something in the panel to make it 220V three phase? In the panel picture T1-T6 is the motor wires at the bottom, The motor wires are T1 to #1 panel wire all the way to T6- #6 panel wire. Also this has a clutch style belt like a snow mobile machine. kind of like a centrifical clutch.I'm no expert here, there's others on this forum that are smarter than me on this type of stuff. That transformer is for control voltage. Yes, it has to be set for the correct voltage going in to provide 115 volts out. The polyphase motor says 208-230 volts. It's definitely a two-speed motor set up to run on 230 volts 3-phase. If I read the tag correctly, wire numbers 1, 2, 3 are for high speed and 4, 5, 6 is for the low speed.
I'm not sure where the 440 volts is coming from, from your original post. Unless there is a BIG step down 3-phase transformer hanging off the back side of the borer. How about some more pictures?
The pictures that have the gold color are my original motor tags from the machine. The tags with red are the reference motor from ebay. Hope that makes it less confusing.Thanks for the confusion... the pictures from another motor.
Get us pictures of the tag on YOUR motor and post. Even if you have to pull the motor to get to the tag. Should be able to squeeze your camera phone in there and take a picture. I done it before. Then report back.
No problem at all, I started adding photos and my Description wasn't very clear at first. I agree after looking this definitely has 2 speeds. The operator panel in front of machine has a high and low speed switch for the main motor. There are 2 sets of control coils (green units in pictures) When you operate the switch between the two speeds one coil activates.My apology. Looks like that motor was rewired for 440 volts. It is a two-speed motor. The only way you are going to make it work on 220 volts is to install a 3-phase transformer to step up the voltage from 220 volts to 440 volts. Or have the motor rewired again back to a 220-volt motor. Or replace the motor with a single speed 220 volt 3-phase motor and power it off of a single-phase input VFD with a 220 volt 3-phase output.
Notice
This website or its third-party tools process personal data (e.g. browsing data or IP addresses) and use cookies or other identifiers, which are necessary for its functioning and required to achieve the purposes illustrated in the cookie policy. To learn more, please refer to the cookie policy. In case of sale of your personal information, you may opt out by sending us an email via our Contact Us page. To find out more about the categories of personal information collected and the purposes for which such information will be used, please refer to our privacy policy. You accept the use of cookies or other identifiers by closing or dismissing this notice, by scrolling this page, by clicking a link or button or by continuing to browse otherwise.