86turbodsl
- Aug 12, 2004
- MI, USA
As in title suggests, i have an application that would be perfect for this type of drive. Does such a beast exist?
I've no idea why the mainstream vendors don't make such beasts.
Fundamentally the only difference is the input rectifier and capacitor bank configuration. Voltage doubling instead of ordinary bridge set up. Everything else is the same and all the active devices sill see the same 230 V nominal (+ voltage boost). Probably less headroom for voltage boost so torque may not hold up so well once you get significantly away from the motor nominal speed. But I suspect that star configuration may be a little less demanding in that respect than delta. In my view anyone who expects to just fit and run a VFD equipped motor outside the "always OK" ± 1/3 rd nominal speed range without doing proper engineering analysis of the set up is asking for trouble.
Naturally you'd need proper input current reduction chokes and a slow charge on start-up routine inside the controller for an industrial rated system. Capacitor bank needs to be larger too. If its a bigger beast some sort of ripple control intelligence via triac type, actively controlled, rectifier is probably a good idea too.
Fixed frequency device as a Phase Perfect, Rotary Converter or whatever replacement ought to be a slam dunk and cheaper for ordinary one to a machine duties. Donkeys years since I built a fixed frequency one, around about the time the first VFD control integrated circuits and output switching devices became reasonable available, and it really can be very simple. Bloke asked me to do half a dozen static converters for his workshop back when even basic rotaries were nigh on unaffordium for average guy and I wondered if a solid state device would have been cheaper and easier. Surplus shop capacitors and the usual futzing around tuning things won out so went no further. In hindsight shoulda run with it.
I have one of the modified breed fixed at 50 Hz running my workshop. 10 HP rated Teco VFD reworked by Drives Direct in the UK around 2005 used in Plug and Play mode via normal machine controls. Treated just like utility 3 phase. Cruel maybe but it hasn't gone pop yet. Largest motor is 3 HP so starting a machine puts significant demands of the overload capacity of the VFD but it can handle it.
Clive
Interesting discussion. Sounds like i need to look harder for a 230V device though. I don't think the power costs to run a transformer 24/7/365 is the road i want to roll down.
And the roughly 160w no load cost to have a transformer plugged in really adds up over time.
Sent from my LG-TP450 using Tapatalk
Based on published data for a 5kw transformer which is appropriately sized.
You don't need switchgear for equipment that runs 24/7 and doesn't get powered off because it's doing something continuously.
They gave you the loss in watts, I assume?
Notice