If you're saying your lathe is single phase 240, it wouldn't hurt a thing to take those two single phase leads out of any box you like. No RPC needed.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
I should clarify. My single phase panel is not in the shop. It is my main 200 amp service for my home.
My supply source for my RPC is the same outlet that supplies my lathe. Ideally I'd like to preserve single phase power to the lathe and have the RPC hardwired so that I can have this 3 phase load center (that will only ever power 3 machines, never simultaneously). If the RPC is not on, and I have wired a single phase circuit from the 3 phase load center, then it is my understanding that I will be out of luck. I don't know how else to make branches in this system.
well...... problem with the wiring.This is excellent, I would never have thought of arranging things in this sequence. I've updated my drawing again to make sure I am understanding you correctly. To answer your other questions first:
Below is my updated diagram incorporating your recent comments. I think my only question is how to ground the RPC panel. Thank you for all the problem solving. It's enlightening.
- My shop 120 is all supplied from my house breaker panel. All wiring is in the walls, including the (3) 50 amp outlets I put in place for my welder and two power hammers. Lighting is the same. The shop is the ground level of a tiny three story home.
- I expect to run everything in rigid conduit. I think I have my wire gauges all figured out now.
- Yes, the RPC panel came from North American Phase Converters and has an integral power switch. They have been very helpful and I have read good reviews of their control panels.
Maybe things are different in Canada, but I see nothing wrong with what he's got going. Not exactly sure what is meant by two lugs on top of each other in the PC box. If that means the incoming and outgoing (if there even is such a thing in AC circuits) single phase connections share parallel lugs in a direct pass thru sort of fashion, then that's electrically no different from what his drawing is doing. Besides... feeding the RPC out of the 3 phase panel allows him to fuse it down with a breaker and run smaller wire then the heavier supply feed. I ran my RPC home system for over a decade wired pretty much like the OP has in the drawing. No problems at all.well...... problem with the wiring.
i own pretty much that RPC
first problem is the lines all over. the NAPC panel has 2 lugs, one ontop of each for the 3 phase.
so the input has to go fully through the panel.
so it would come into the garage, go through the pull down shut off, then go into the phase coverter, L1 and L2
the other L1L2L3 will have the bottom lug set go to the motor, then top lug set go to the 3Ph panel. just creates a wiring mess.
if you want a 1PH panel, by code it needs to be separated. they are under $100. much cheaper then a pull down switch plus fuses which can be $200.
True, although a 3-pole breaker would give those same advantages (at higher cost). I'm not sure that you're gaining much in wire size going from probably a 40 to 60A breaker. Depends on distance from panel to RPC.The 2 pole breaker feed to the RPC allows smaller wire and allows his single phase lathe to remain running should he need to do something with the RPC concurrently.
The issue is that while they won't *successfully* start, the contactor would still pull in, livening L3 via the motor windings. Granted, it should be *close* to neutral potential, and that's mostly an issue if you have someone else that wants to use the tool, and doesn't check to see if the RPC is running first.The only time you could start another machine with the RPC disconnected would be if another 3 phase machine of larger HP was already running. If the RPC is out and no other machine is running, no 3 phase machine will start.
Fair call, but given the desire to run single-phase equipment without the RPC running, this requires a second panel or new home runs. I think it's been debated further upthread.power supply and power distribution needs to be separated. this way if one leg drops out, it will shut down the unit and not burn up machines down stream by single legs missing.
Absolute BS for mains frequency AC with wavelengths of literally thousands of miles/kilometers. Phase shift from lightlag is something that can be ignored even by utilities. Volt drop from extra conductor impedance can occur, but would be difficult to measure on a balanced three phase system, let alone have a significant impact on a system with an RPC that's inherently miles from being perfectly balanced.also makes for a cleaner sine wave form being direct to the motor on all 3 legs to keep the phase shift in sync.
Notice
This website or its third-party tools process personal data (e.g. browsing data or IP addresses) and use cookies or other identifiers, which are necessary for its functioning and required to achieve the purposes illustrated in the cookie policy. To learn more, please refer to the cookie policy. In case of sale of your personal information, you may opt out by sending us an email via our Contact Us page. To find out more about the categories of personal information collected and the purposes for which such information will be used, please refer to our privacy policy. You accept the use of cookies or other identifiers by closing or dismissing this notice, by scrolling this page, by clicking a link or button or by continuing to browse otherwise.