I am wiring up my new 30 hp RPC and my new-to-me VMC this weekend. I need to run 36 feet of wire from the breaker panel to the RPC (up a wall, across the ceiling and down to the RPC).
The RPC requires a 70 amp breaker. It can draw up to 70 amps on start up and idles at 15 to 20 amps.
According to the VMC's manual, the Sharp SV-2412SX 3 phase power requirement is 18 KVA or 44 FLA according to this calculation (18*1000)/(1.732*.98*240).
Various wire charts show #6 THHN is rated at 75 amps. So I would like to run #6 stranded copper THHN from the panel to the RPC.
Anyone have any concerns with using #6 stranded copper THHN for this setup?
The RPC requires a 70 amp breaker. It can draw up to 70 amps on start up and idles at 15 to 20 amps.
According to the VMC's manual, the Sharp SV-2412SX 3 phase power requirement is 18 KVA or 44 FLA according to this calculation (18*1000)/(1.732*.98*240).
Various wire charts show #6 THHN is rated at 75 amps. So I would like to run #6 stranded copper THHN from the panel to the RPC.
Anyone have any concerns with using #6 stranded copper THHN for this setup?