Vancbiker
Diamond
- Joined
- Jan 5, 2014
- Location
- Vancouver, WA. USA
Your page describing the EX193 alarm says that input X20.5 is the spindle amp rigid tap ready signal while the page from the wiring diagram says it is input X0.2. This conflicting info makes troubleshooting a bit harder.
In your wiring diagram, find a Y address that is connected to a signal at the spindle drive labeled TLML and post a pic of that page.
Check that spindle drive parameter F31 is set to 1.
In your wiring diagram, find a Y address that is connected to a signal at the spindle drive labeled TLML and post a pic of that page.
Check that spindle drive parameter F31 is set to 1.