When dealing with issues like this, I like to make sure that the basics are covered. Usually capacitive coupling is playing a role and circulating currents can bite you too.
I like the idea of disconnecting the load on the breakers that trip and seeing what happens.
But circulating currents can be nasty. Remember that the neutral gets bonded to ground at only one point! And only at one point! It is usually at the service disconnect which is usually the first electrical panel. From there, any sub panel(s) must have the neutral and grounds separate - this means that the sub panel cannot be only service entrance rated - must have the capability to remove the neutral to ground bonding jumper and have separate ground and neutral rails.
As stated earlier, you must use a 4 wire (2 hots, neutral and a ground) from the service entrance electrical panel to the sub panel, and from that sub panel to the next sub panel. From there, make 100% sure that the neutral and ground are separate in both sub panels and that you have not crossed a neutral and a ground. Grounds must go the the ground bar and neutrals go to the neutral bar!
I can't tell you how many times I have seen this violated in the industrial world and sometimes it causes nasty electrical gremlins.
I like the idea of disconnecting the load on the breakers that trip and seeing what happens.
But circulating currents can be nasty. Remember that the neutral gets bonded to ground at only one point! And only at one point! It is usually at the service disconnect which is usually the first electrical panel. From there, any sub panel(s) must have the neutral and grounds separate - this means that the sub panel cannot be only service entrance rated - must have the capability to remove the neutral to ground bonding jumper and have separate ground and neutral rails.
As stated earlier, you must use a 4 wire (2 hots, neutral and a ground) from the service entrance electrical panel to the sub panel, and from that sub panel to the next sub panel. From there, make 100% sure that the neutral and ground are separate in both sub panels and that you have not crossed a neutral and a ground. Grounds must go the the ground bar and neutrals go to the neutral bar!
I can't tell you how many times I have seen this violated in the industrial world and sometimes it causes nasty electrical gremlins.