480 volt transformer tripping breaker
Page 1 of 2 12 LastLast
Results 1 to 20 of 37
    Jun 2007
    Vancouver Island, B.C. Canada
    2,033
    47
    253
    Default 480 volt transformer tripping breaker
    I have a mystery problem.
    I have 120-208 volt three phase coming into the building.
    I installed a 120/208 to 480 volt 30kva transformer to run my large roller.
    At the time I installed a 30 amp 3phase breaker to run the transformer from the 120/208 panel.
    This worked well and perfectly for a few years. Then I needed to upgrade the panel and I also needed to run my 480 volt plasma machine from the same transformer. The wires are sized correctly for the load. I have an electrician friend that does most of the work and I just help with the grunt work.
    We upsized the breaker to a 50 amp from the main panel and that is when the trouble began. The breaker trips every time I turn on the transformer. It happened the very first time and there was no load on the transformer. Reset the breaker once or twice until it will stay and then it is fine? Why is this happening?
    It is very annoying to buy a $300 breaker and have it perform this way. The 30 amp breaker did not trip. The transformer is controlled by a mag switch which uses a separate 120 volt circuit for the coil. Also the first 50 amp breaker was returned and replaced as we thought it the culprit. Seimens brand equipment.
    Any ideas from all you electron experts?
    Thanks!
    Michael
    Aug 2014
    bainbridge island
    1,394
    306
    344
    The new breaker is most likely tripping on the magnetic effect of the surge current, not the thermal rms Heat produced by the current.
    Try powering the transformer through 3, 50 to 80 amp slow blow fuses.
  3. Likes TDegenhart liked this post
    Oct 2017
    1,310
    417
    446
    Check the trip curve between the two breakers.
  5. Likes JST, TDegenhart liked this post
  6. #4
    Jun 2001
    St Louis
    19,209
    2367
    3593
    Depending on brand of panel, there may be a surge resistant type of breaker available. Typically that is one made for HID lighting.
  7. Likes TDegenhart liked this post
  8. #5
    Jun 2007
    2,033
    47
    253
    Thanks for the fast replies.
    I could power this through a fused disconnect but the panel was working fine with the exact same setup with the 30 amp breaker.
    Not sure how to test the trip curve? Can you elaborate? This is a three pole breaker?
    I could try to find out if a surge resistant breaker is available but it sounds like a pile of cash and I am pretty sure they won’t take back the 50 amp I already have.
    Can anyone elaborate on why the 50 amp breaker performs poorly and the 30 was fine? There is no load on the transformer when I turn it on, so the surge is from the transformer windings? Is this just a quirk of the magnetic effect?
  9. #6
    Nov 2013
    Eastern Massachusetts, USA
    7,011
    5969
    6391
    Circuit breakers have various trip times. You need one rated for surge current due to magnetic inrush. This is common with large transformers and motors. Likely your old breaker was a bimetal type that had to heat up before tripping. The inrush current occurred over too short a time to trip it. The newer ones will trip very rapidly unless you use a model that has a built-in mechanical delay.
    The reason for the high current when first switched on even when unloaded is because the more efficient core steels often tend to act as if there is no core, only a loop of wire for several milliseconds at first application of power. The "stiffer" the source is the worse the inrush.
  10. Likes Strostkovy liked this post
  11. #7
    Jun 2007
    2,033
    47
    253
    Scottl,
    Thanks for that clear explanation. I understood the first part but not the second.....
    Not sure why the manufacturers need to “improve” things all the time.
    Luckily it is only 20 feet to the panel but it sure is annoying.
  12. #8
    Oct 2017
    1,310
    417
    446
    Quote Originally Posted by M. Moore View Post
    Scottl,
    It's likely not an "improvement" and more that you just bought the wrong breaker.
    There have always been multiple options for trip curves and I believe Siemens sells them A, B, C, or D with A being for resistive loads and D being for very hard starting loads or fire pumps or whatever. If you want a higher trip curve than that you'll need to find an old Zinsco panel.
    Check the part numbers of your new and old breakers.
  13. Likes johansen liked this post
  14. #9
    Mar 2009
    Eureka, CA
    4,374
    1022
    1757
    Not reading all the posts, I have a question...why are you switching this transformer ON and OFF. I've had a ton of equipment on transformers and they stayed ON for years, ad nauseam. Maybe your situation is different.
    Stuart
  15. #10
    Jun 2007
    2,033
    47
    253
    Stros,
    Thank you for that info. I relied upon my electrician to buy the breaker. I believe we both thought that starting a transformer was not a big load therefore didn't need any special kind of breaker and we were using a larger breaker than had been installed prior. So this transformer should have a C or D rated breaker?
    Atom,
    I have two transformers in my shop and turn them on when needed. No need to run them all the time for just occasional use and they both buzz which annoys me when the shop is quiet. Most of my equipment runs off the 208 three phase power and I have quite a lot of equipment for a one man shop....
  16. #11
    Virginia
    19,738
    7561
    11862
    Stros,
    Atom,
    Wise to OFF them.
    That annoying buzz is just a "memo"... that you are PAYING for what causes it!
    PS: Your electrician is uncommonly ignorant. "Residential" guy, not commercial? Worse than that.
    They are neither of Physicists nor Hairy-ears.
    But they are MEANT to KNOW about the appropriate selection amongst the many and several options of breakers, fuses, load centers, and switchgear as well as conduit and wire sizings.
    Or know where TF to FIND OUT and WHEN they NEED to go seek!
    Seriously. Makers freakin' trip OVER themselves competing to make good info dead-easy to find. So they get the design-win.
    He's missed the "basics".
    Even BEFORE s**t as DOES change over time does the usual. So, too does "the Code" evolve, BTW. Meant to keep current with THAT, too. Code has added about 700 pages over my notice of it. That's only a rate of change of ten pages a YEAR. BFD.
    Whom ELSE do you expect to be in the know? The lawn-care guy? Your dentist?
    "Inspire him". To catch-up... and keep on so-doing.
    Or fire him.
    Before he gets you hurt in body, or a fire.. not just weaker in the wallet.
  17. Likes steve-l liked this post
  18. #12
    Mar 2012
    Geilenkirchen, Germany
    2,862
    1608
    1498
    All inductive loads have inrush currents. Some,depending on several factors, can be thousands of amps. These large inrush currents not only pop breakers, but are unhealthy for other equipment connected to the street distribution transformer, potentially pissing off your neighbors. These can be avoided easily by using soft start techniques. The most simple one is 3 incandescent light bulbs, one per phase in series with the input windings of the transformer. When these are in circuit, the max current will never exceed the resistive current of the bulb. Before applying any load though, you need another switch that shorts around these bulbs. That switch would then have two positions, Start and Run. Easy inexpensive solution.
  19. #13
    Virginia
    19,738
    7561
    11862
    Quote Originally Posted by steve-l View Post
    Sheesh. Talk about bright ideas...
  20. #14
    Mar 2012
    2,862
    1608
    1498
    Interestingly, the inrush duration is too short to light up the bulbs.
  21. Likes JST liked this post
  22. #15
    Nov 2013
    7,011
    5969
    6391
    A more "industrial" solution is to insert NTC thermistors in series with the load, with a relay that will short them out after a brief delay and also reset on power-off. This way the thermistors can cool down before the next time power is applied.
    The manufacturers make thermistors specifically intended for inrush limiting and provide guidance on selecting the appropriate parts.
  23. #16
    Jun 2007
    2,033
    47
    253
    Two questions, if the breaker is designed to break easily and does so when switching on the transformer why does it hold if I reset? Often once will do it but usually have to reset twice.
    Second, none of the information found so far has any info on different choices of breaker, from what I can see there is only one choice in a 3 phase breaker from Siemens, however they may be available by special order but I can’t find the info. So where to find this info?
    The light bulb solution sounds good but it seems like a new breaker would be far simpler. Or a little more work to change to a fused disconnect. My wall is nearly full of disconnects but I may be able to rearrange things.
    Are there any other ways to massage the voltage?
    No complaints...I know it was three questions!
  24. #17
    Jul 2007
    Missoula Mt
    1,365
    58
    639
    Not a big deal you (not knowing anything about breakers ) bought the wrong breaker.. buy a breaker with a adj mag trip made for electric motor starting ( and transformers) will cost more $$ but will work...what not to like??...Phil
  25. #18
    Jun 2007
    2,033
    47
    253
    Scottl was typing as I asked the question.
    There are 5000 types of NTC thermistor listed on Mouser electronics...the good news is that they appear very inexpensive if only I knew which type to buy?
  26. #19
    Jul 2007
    Missoula Mt
    1,365
    58
    639
    A NTC thermistor will nothing for you, it is the inrush amps thats kicking the breaker...Phil
  27. #20
    Jun 2001
    St Louis
    19,209
    2367
    3593
    Quote Originally Posted by Phil in Montana View Post
    probably won't, but only because the proper one for the current will likely not have a high enough resistance. And one that does, probably will not last.
    They perform the right action, but may not be sufficient.
