Don Gitzel
- Jul 25, 2017
The intention is to feed this auto transformer with 230 volts from rotary phase converter. Will it work if I disconnect all reference to ground!View attachment 2
The intention is to feed 230 3 phase from a rotary phase converter into the low voltage side of the auto transformer X4-X5 & X6 and get 600 volts out of H1-H2 & H3 to feed a machine. View attachment 295604
With regard to grounding....
First, you absolutely cannot ground the X0 connection, because the output of a phase converter is NOT balanced to ground, and this is an autotransformer, which is not isolating.
The phase converter puts out wild leg 3 phase, which is grounded at the center tap of the source 230V. That is NOT the center of the 3 phase output.
So:
1) the output does NOT form a "separately derived source", so rules on grounding such a source do not apply.
2) The center "X0" is NOT at ground potential, it is at a substantial voltage to ground, so in any case it cannot be grounded.
3) None of the wires from the phase converter can be grounded either, they are all at a voltage to ground, so corner grounding is not possible.
4) The source for the 3 phase converter IS grounded, and that will supply the ground reference for that entire circuit. No further grounding is allowed.
Bottom line: Do not ground any part of the phase converter or this transformer. The bonding is (or had better be) back at the service box, and no further ground connections are necessary (nor are they allowed).
You need to connect the x0 "neutral" of the auto transformer to the y neutral point of the rpc. (T 4 5 6 for a 9 wire motor)
Notice