Compact Aluminum wire for new shop. Any good?
Page 1 of 2 12 LastLast
Results 1 to 20 of 24
    Mar 2007
    Wisconsin
    156
    14
    58
    Default Compact Aluminum wire for new shop. Any good?
    We are all aware and have read of the problems with aluminum wire. So, we are building a new shop, one of the electrical bidders come in and I ask if he is using copper. "No, we use compact aluminum". No, I say, I want copper; aluminum is too much hassle for me. He replies with reassurance that this is not the aluminum of the past. He's been installing this for years without issues....blah, blah, blah. I've never actually heard aluminum wire called "compact" before. Is this actually an improved product or still the same turd with a different colored bow?
  2. Likes Zahnrad Kopf, Mark Rand liked this post
  3. #2
    Mar 2011
    Geneva Illinois USA
    6,343
    2749
    2469
    First issue is it's your building. If he doesn't want to do copper, then find another contractor. I agree with using copper.
    There have been advances in aluminum wire since the 60's and 70's. The power companies routinely use aluminum, but then that know how to use it. Lets say that you do go with aluminum. In a few years the system needs work for whatever reason. Will the new electrician know how to handle the stuff? Copper is probably more expensive but is it worth the risk?
    Tom
    edit:- Do a Google search using "nec code aluminum wire" or other search term. Compacting means the space between the strands as be eliminated meaning that the wire acts like a solid conductor, not stranded. Further, alloy additions have reduced the cold flow of old al wire. You are still restricted on terminating the wire as in twist on connectors cannot be used to join al to cu wire. Some connectors require anti-oxidation compounds, others don't.
    Your choice.
    Tom
  4. Likes grounded-b, ranchak liked this post
  5. #3
    Apr 2010
    Wisconsin
    6,154
    4218
    3827
    Tagged, subscribed, and watching because we're in the same boat...
  6. Likes BSCustoms liked this post
  7. #4
    Apr 2018
    Wisconsin
    6
    I am sure your contractor meant that he uses compact aluminum wire for the "big stuff" - feeders to panels, large machines (over 60A) and the like.
    In these cases, aluminum wire can be terminated easily. Most all lugs are dual rated - copper/aluminum, just clean, apply No-Lox, and torque to spec.
    Aluminum should NOT be used for branch wiring - outlets, switches, lights, etc.
    Just my humble opinion.
    Steve
  8. Likes Pete Deal, TDegenhart liked this post
  9. #5
    Apr 2010
    Wisconsin
    6,154
    4218
    3827
    Quote Originally Posted by grounded-b View Post
    Steve
    So, as this is your first post, welcome to the forum. Hopefully this does not derail FK's thread at all, but in the hopes that it is relevant ( to both he and I ) - Where in Wisconsin are you and what do you do for a living?
  10. Likes Pathogen liked this post
  11. #6
    Mar 2007
    Wisconsin
    156
    14
    58
    Steve
    That is pretty much the impression I got from him as well. And to be clear, this is not a "bash" on this guy. He actually seems very intelligent, honest and straight forward. Doesn't seem to be "selling" me on an inferior product. He is willing to put in copper, just said that this aluminum works and obviously is cheaper. I've just never heard of "compact aluminum" before. Was it always called that and we just refer to it as aluminum wire? Or is it something new/improved to handle the issues of old.
  12. #7
    Jul 2014
    MI USA
    928
    200
    381
    Here is an example of a compact conductor.
    Were not in the 60's any longer, and neither is the aluminum alloy used for conductors. Many of the bad experiences were from internal house wiring, and installations where the equipment terminations were not designed to allow for aluminum conductors. There was a problem with thermal expansion and corrosion in the early products. It still has a greater coefficient of expansion, under load than copper, but not near as bad as it used to be.
    Earlier products needed to be wire brushed to remove oxides immediately before termination, and then coated with anti oxidant compound to prevent future oxidation. This is no longer required, but is still a good practice, especially where terminated outdoors.
    Most distribution equipment lugs today are made of the same material and are approved for either type metal. With termination lugs of the same material, the temperature expansion is less of an issue as they expand at a similar rate.
    This conductor is used for services and large feeders almost exclusively today, especially on large and long runs, to reduce cost. However it needs to be up sized from an equivalent copper conductor, which means that the conduit needs to up sized as well.
    It isn't even offered in individual conductors in small sizes generally, as would be used in branch circuits for equipment and general loads. The exception is in home cables such as for a range, A/C or dryer circuits.
    The most cost savings can be had with underground use, with PVC conduit, as compared to rigid steel conduit and copper conductors. If the circuits are oversized, from the bare minimum requirements, that reduces most of the expansion from running under loaded conditions.
    Even many distribution transformers are wound with aluminum wire today, and terminated in aluminum lugs.
    The long term reliability of aluminum is really dependent on the selection of material, insulation type and installer skill. It can be used effectively to reduce cost, dependent on conditions. It is widely used, and stable when done properly.
    Copper is still the premium material. Conducts away heat better. Less corrosion effects, and the corrosion is still conductive. Best used for heavy demanding loads and all internal building small feeders and branch circuits. But comes at a premium price.
    Any competent electrical contractor should have no problem pricing a job with either material, where it is appropriate for use.
    SAF Ω
  13. Likes Milland, grounded-b liked this post
  14. #8
    Mar 2011
    Geneva Illinois USA
    6,343
    2749
    2469
    Quote Originally Posted by SAF
    Less corrosion effects, and the [B
    corrosion is still conductive[/B].
    SAF Ω
    Copper oxide is a semiconductor. Remember copper oxide rectifiers?
    NEMA had a 8 hour temperature test in the 1930's or so to make sure that the copper switch contacts didn't go into thermo runaway because of copper oxide creeping in between the contacts.
    Tom
  15. #9
    Jul 2014
    MI USA
    928
    200
    381
    Copper oxide rectifiers were a bit before my time, I worked with a few selenium ones though.
    So can you tell us what the results of the NEMA temperature test were, Did the contacts pass the test?
    SAF Ω
  16. #10
    Apr 2018
    Wisconsin
    6
    Quote Originally Posted by Zahnrad Kopf View Post
    Industrial electrician living in Milwaukee, WI
    Found this forum because I have to repair a 1960's Monarch 10EE lathe. With the vacuum tube motor controller
  17. #11
    Apr 2010
    Wisconsin
    6,154
    4218
    3827
    Shoot me your information if you are open to it. We are in the process of looking for a building or the land to build one upon. Once that happens, electrical won't be far behind and I refuse to do it the hard way again. I can be reached through the forum via email or private message, as well as the contact page from our website. ( American Machine & Gear Works ) Thanks.
  18. #12
    Virginia
    29,030
    7561
    9022
    Quote Originally Posted by TDegenhart View Post
    "in a few years" any sparks as does not ALREADY have the knowledge will have to have acquired it.
    Copper is waaay more expensive, "relatively" than it once was, and we are not going to be seeing much of it for feeders within a commercial building in future any more than we have seen it very much on the feeds TO buildings and residences for rather a long time now since the first major changes to what HAD been an all-around problematic alloy, and is no longer much of a negative atall.
    I still do not LIKE Aluminium, personally.
    But WTF? Other fish to electrocute.
    I can't be bothered trying to boil that particular part of the ocean.
    I suspect that in the same boat, my idea of "premium quality" might be to pay for a one-size upgrade to Al distribution conductors rather than to insist on Cu at far higher premium cost.
    A failed or failing termination INSIDE an industrial load center is seldom a disaster, nor even close, anyway. Part of why they even exist is a "containment" function.
    It was back when Harry Homeblower had it inside walls and such and knew not, that it was setting homes afire.
    Primary service entrance load centers, utility company side, especially, didn't have huge issues even back when the Alloy had nasty creep. Higher maintenance costs, yes. Hollywood-level drama, with fire bombs and car chases? Much less-so.
    2 ..... aluminium East German coins worth,
  19. #13
    Mar 2009
    5,372
    97
    1020
    Quote Originally Posted by FK View Post
    Ask for references. Ask what they think.
    The power company out here uses stranded aluminium for the main power ground. The only issue I have is when the squirrels chew on it to sharpen their teeth. Chewed it in half. The power company guy said if it was up to him he would issue a few thousand air rifles to customers, to cut down his work load.
  20. #14
    Jul 2010
    Rochester, NY USA
    2,223
    10
    526
    I personally don't like Aluminum for machine drops where there is any kind of vibration.
    Most machine connections will require lugs rated for Aluminium, most are not.
    The same goes for older breakers and buss duct plugs.
    So copper is a natural in these cases.
    Bill
  21. #15
    Virginia
    29,030
    7561
    9022
    Quote Originally Posted by hitandmiss View Post
    Bill
    Actually a great deal of new manufacture IS "AL-CU" rated and so marked. Likewise your sparks travels with Al-Cu splice and lug hardware in the truck. It is even on the wall at most Big Box.
    That said, I do NOT want Al leaving the entrance / main distribution load centers.
    Breakers and beyond? The runs are shorter, the switchgear, conduit, hangars or other support anchorage, bonding & grounding, and labor cost is significant, regardless, and the premium for copper just one cost element among many.
    That makes the last few yards of it more affordable "relatively" in the overall costing of the whole job, so there isn't much to justify declining savings.
    Just use Copper. It is indeed a "natural". Then go resolve some more pressing issue that is less-so.
    2 COPPER CW
  22. #16
    Jun 2001
    St Louis
    18,210
    1959
    3093
    About that 10EE, you have no doubt found the section here on Monarch.... Should be lots of help there. I was even at one time working on a solid state tube replacement for those, but the demand seemed low.
    Aluminum wires? It could be worse... How about sodium electrical cables?
    Evaluation of Sodium Conductor Power Cable
  23. Likes grounded-b, Rigor liked this post
  24. #17
    Mar 2011
    Geneva Illinois USA
    6,343
    2749
    2469
    Quote Originally Posted by JST View Post
    Just don't get the conductors wet or have any nicks that would expose the sodium to moisture. All terminations would have to be in oil.
    Tom
  25. #18
    Virginia
    29,030
    7561
    9022
    Not so fast, McGee!
    Superconductors have been in use for a while now, out Asia way, where population densities are borderline insane (or maybe well-beyond just "borderline" ?) and space for transmission facilities is worth Gold, not Copper. Major producers, of course, include Japan ..and China.
    "http://www.furukawaelectric.com/fehk/en/product/energy/power_cable/sc.html"
    "https://asian-power.com/project/news/shanghai-electric-cable-expands-alliance-amsc"
    Advances have kept coming.
    Note the stats in this old article as to how much our (heavily Aluminized?) grid wastes in the USA. Not bad as a percentage. Not bad atall if you've ever had to distribute over the distances we have vs Europe.
    Still.,, staggering in MW:
    World's first superconducting power line paves the way for billions of dollars in savings, more nuclear power stations - ExtremeTech
  26. #19
    Jun 2001
    St Louis
    18,210
    1959
    3093
    Tom
    Surprisingly, the data I saw did not support extreme measures. Insulation was polyethylene, and connections were not an issue. Holes in the insulation were actually found to get sealed off by corrosion products.
    Biggest issue was apparently the near zero tensile strength of the material.
    There were some underground cables put in and used for some time, apparently. I notice that they are not STILL used, however.
    It made some sense, as there s a lot of sodium available.
  27. #20
    Virginia
    29,030
    7561
    9022
    True enough. But there is twice as much iron, three times as much Aluminium, and ten times as much silicon in the lithosphere - all of them easier to handle with little or no special care - as well.