Electric heat treating oven - Page 2
Page 2 of 2 FirstFirst 12
Results 21 to 23 of 23
  1. #21
    Oct 2004
    Elyria Ohio
    1,785
    3358
    728
    Quote Originally Posted by Toms Wheels View Post
    Your issue is that a phase converter would need to be connected to the thermostate of the furnace, and controlled by that, not relays switching the load lines. An RPC would handle your issue fine, or the rewiring you are considering.
    Tom - thanks - I will try re-wiring to make is single phase. I don't really see a down side. Both sets of heater elements want to see 220v - right? To my mind, what difference does it make if they are seeing 220v from L1/L2 or L1/L3 - yes?
  2. #22
    Aug 2014
    bainbridge island
    1,130
    215
    267
    you got close with your drawing but one of the elements is not getting power.
    in the drawing you have two relays, from the top down they get power on the left side from L1, L2, L3, L3
    the input sides of the relays need to be L1, L2, L1, L2.
    as it is marked now, one of the heating elements is not getting any power because its connected on both sides to L2.
    yes you could remove one of the relays, but they may not be rated for 43 amps.
  3. Likes motion guru liked this post
  4. #23
    Oct 2004
    Elyria Ohio
    1,785
    3358
    728
    Quote Originally Posted by johansen View Post
    johansen - you're talking about the elements on the right side? So if I switch the top of the lower relay to L1 the nearer of the two right-side elements will terminate in L1?