Richie V6
- Oct 18, 2012
- Chicago IL
Hello All. We recently moved into a new commercial faculty. We are trying to figure out our high power consumption. Our first bill showed a use of 3400kWh while we were moving. During the move we did not use any equipment other than computers, lights and AC for a 1500SQFT office.
We did some digging and found that our Delta-Delta 480V to 240V transformer was putting out a lot of heat. We shut off all the loads on the secondary and measured input current on the primary.
Primary input current (No load)
L1 = 8A
L2 = 8.4A
L3 = 11.5A
Is this typical input current for a unloaded 150kVA transformer?
I just did some more detailed measurements with equipment running and it appears the primary input current is unbalanced. However the voltages are close.
Primary input current (Loaded)
L1 = 29.2A
L2 = 11.4A
L3 = 34.5A
Primary phase to phase voltages (Loaded)
L1-L2 = 494V
L2-L3 = 491V
L1-L3 = 491V
Primary phase to neutral voltages (Loaded)
L1 = 284V
L2 = 285V
L3 = 283V
Secondary phase to phase voltages (Loaded)
L1-L2 = 247V
L2-L3 = 244V
L1-L3 = 243V
Secondary phase to neutral voltages (Loaded)
L1 = 122V
L2 = 213V
L3 = 122V
I called the utility out and they claim the power outside of the building is fine. My electrician thinks the utility is sending us unbalanced power causing the transformer to heat up.
Any ideas? Any help would be appreciated.
L1 = 8A
L2 = 8.4A
L3 = 11.5A
L1 = 29.2A
L2 = 11.4A
L3 = 34.5A
L1-L2 = 494V
L2-L3 = 491V
L1-L3 = 491V
L1 = 284V
L2 = 285V
L3 = 283V
L1-L2 = 247V
L2-L3 = 244V
L1-L3 = 243V
L1 = 122V
L2 = 213V
L3 = 122V