Lenze Ac Tech wiring diagram for 4 I/O connectors
lazz
Stainless
Feb 12, 2012
The warm desert of Phoenix Arizona
I have a Lenze Ac Tech Model ESV402N02TXB571
The VFD is connected to a lathe forward/reverse and speed control function.
This model has only 4 connection terminals rather than the regular 14 shown in the online manual.
I would like the VFD to start the motor when it powers on. The manuals found show how to do this with a 14 connection I/O but not a 4 I/O connector. The manual mentions #1 and #4 are used for auto start. This VFD has terminals numbered 1,11,2,30.
Any suggestions?
You have a different model which the controls are via the Dual port RJ-45 For Modbus RS-485 Daisy Chaining. This is a 3 phase input VFD, would need to be derated for single phase.
There is a program parameter for auto-start on power up, but manual does not specify if it also needs a run command.
P10 = 1 Start on Power-up
P100 = 0 (default) Start controls via front panel.
Thanks all..
This has been resolved...
I can start on power up with a jumper between #1 and #11. Provided P100=1 and P110=1.
TO restart the drive I will need to install a switch between #1 and #11 or power off the drive.
Once again VFD's are hard.
There is a note about the start comment in the margins of P110.
P110 = 1, 3…6: For automatic start/restart, the start source must be the terminal strip
and the start command must be present.