Got a new 5hp compressor, and it was running fine for a while.
All of a sudden it started tripping the main breaker, and not the breaker that its connected to.
Main Breaker is 100amp, Breaker of the compressor circuit is 40 amp. The circuit is not new, already had it and it worked fine with my welder.
So I checked the other day, when compressor started up and running, with a few small appliances on in the house, the entire panel was seeing a total of 43 amps, well below the 100. Obviously that day when testing, it didn't trip.
But a few days later the problem was back.
So today, I turned off all the breakers, except the one the compressor is connected to. I left the drain open and it ran for a while, never tripped the breaker. Total panel was seeing about 35 amps.
Then I started turning on the other breakers, and the main breaker tripped almost immediately. Turned the compressor off, and checked the entire panel was only pulling 4 amps. So definitely wasn't a combined load issue, as compressor draws about 35 plus the 4 from various other items that were on.
Any idea what could cause this ?
Could it be some kind of faulty wiring on another circuit,that is causing this, and it only trips when a large amount of amps are being drawn, even though its on a different circuit. Seems kind of weird though.
I'm thinking of disconnecting all the wires from the other breakers, and letting the compressor run. If it still trips its an issue with the Panel/Breakers, if it doesn't it must be a wiring issue.
Any help would be appreciated.