Just a bit more explanation.
A dual Voltage (115/230 VAC), motor will have two coils and they are wound in the same position, on top of each other, if you will. Each of these coils will be designed to be connected to 115 VAC. When the motor is configured for 115 Volt use, the two coils will be connected in parallel and each will be connected to the 115V supply.
But when it is configured for 230V use, the two coils will be connected in series. Being connected in series and also having the same number of turns and made with the same gauge wire, those coils will have the same resistance (impedance actually) and they will form a Voltage divider that is connected across the power line. Since the resistance is equal, they will divide that 230 Volts in half and each coil will "see" the 115V that it was designed for.
The inner workings of the motor will show absolutely no difference when these two types of connection are used. The magnetic fields will be identical at every instant in time. The torque will be the same. The HP will be the same. The start-up times would be the same. The amount of heat generated would be the same. In fact a sufficiently small midget with an array of small instruments who is confined to the inside of that motor, not including the connection panel or a Volt meter connected to the ends of the coils, would have very little in the way of determining which Voltage the motor was connected. The motor's operation is really exactly the same in each configuration.
Externally the 115V configuration, with the two coils in parallel, will draw twice the current as the 230V, serial connection. Thus the power, which is given by Voltage X Current will be the same in each case.