Laverda
Cast Iron
- Mar 24, 2014
- Riverside County, CA
I think my electrician is wrong!
Building a new workshop 250' from main house breaker panel. Panel upgrade finished to 200 amp and 250' of 2AWG, four conductors run to sub panel on shop. Before slab was poured. 24' of copper grounding rod put in ground and is also bonded to the re-bar.
When sub panel was put in and wired up the electrician bonded both neutral and ground to the sub panel box. he did not use my earth ground at all and stated "it was not required by code and the ground wire back to the main panel would take care of the earth ground".
I was surprised when I saw him do this but he stated what he did was to code. He has been in business for years.
As far as I know you never want the return current on the ground wire at all. And if the neutral has a fault, all return current is now on the ground wire and hence anything metal in the shop that has a ground back to the panel, including the panel itself could have voltage on it.
Should be easy to research, but what I have found is depending on who you ask and where in the country you are at you will get a different answer.
I have read:
Don't need a ground from main panel at all and use the grounding rod at the shop. Some say to bond the neutral and ground at the shop some say not to.
Some say what my electrician did is OK.
Some say neutral and ground should not be bonded and ground from main panel should connect to ground on shop panel and then to earth ground rod at shop. So the only time the ground will see current is if hot touches something metal. This is what I think is correct.
So who is correct?
I have read:
So who is correct?