kb0thn
Stainless
- May 15, 2008
- Winona, MN, USA
Hi Guys,
I have 208V 3 phase power at my main shop. At my home shop I have 240V single phase. Been running most stuff off of VFD and have been using diesel generators for occasionally used 3 phase equipment. But now have purchased a large format CNC router and I want to run from grid power and not diesel. It's got a multitude of motors and pieces that use three phase. So VFDs aren't a reasonable option for it. And I'm somewhat keen on having plug compatibility between the shops so I can move equipment back and fourth.
So I've purchased an American Rotary 25HP control panel and have a Baldor motor that is going with it.
My understanding is that the output from this RPC will be delta. And that if I want wye, I need a delta wye isolation transformer. Given the size of the RPC, I need the next size bigger than 30kVA. Which should be 45kVA.
Much searching has lead to:
TESTED MGM HT45C3B2SH 45 KVA STEP DOWN TRANSFORMER 240V to 208V 120V 3-PHASE | eBay
Questions:
1) is this the right transformer for what I want?
2) hookup to meet NEC 2017
a) obviously 3 phase delta from RPC in the H1 and H2 and H3 connections
b) obviously 3 phase wye out to panel from the X1 and X2 and X3 connections
c) X0 is my derived neutral. It goes to my neutral bus in my 3 phase wye panel
d) X0 gets bonded to ground. I believe that happens in the transformer and the neutral bus is isolated in the panel. IE no green bonding screw in the panel.
e) additional ground rod required at the the transformer. And bond to building structural steel / metal water pipes in that area. Wood frame building and no metal water pipes, so not much I can do there.
f) output of RPC is protected with 70 amp 3 phase circuit breaker at the RPC. That's about 60 feet from where the transformer and wye panel is. That provides over current protection for the wire. Presumably that also provides protection for the transformer primary.
g) is over current protection required on the secondary of the transformer? IE can I just connect the output to the main lugs on the wye panel or do I need breaker or fuses? Intuitively it seems to me that the 45kVA transformer should be protected fine with the 70A breaker on the primary side. But I'm not at all familiar with the NEC with respect to transformers.
h) Am I missing anything?
Thanks, thanks, thanks!
-Jim
Questions:
-Jim