sizing a control transformer
Results 1 to 8 of 8
    Aug 2007
    GA
    802
    138
    Default sizing a control transformer
    I need to build an estop circuit with a transformer that will hold in a 24vac coil on a contactor that has an inrush of 200va, "sealed" 24va, heat dissipation 10w. what VA 240v to 24vac transformer do I get?
    Mar 2011
    Geneva Illinois USA
    6,423
    2807
    2509
    Is this a long control line as in 20-30 feet from the contactor? If so then the resistance and capacitance of the wires have to be taken into account. A good introduction to calculate the size transformer is in this reference.
    http://dl.icdst.org/pdfs/files3/10b9...774ff2f1d8.pdf
    Just from experience I would say 75VA minimum.
    Tom
    Aug 2007
    GA
    802
    138
    Pretty short line, the estop button and transformer are in the same 3' x 3' x1' cabinet...Good paper, that..75-100va it is.
    Dec 2019
    NEW ZEALAND
    106
    23
    If it's all in the same cabinet, just use a 240V contactor. Your switch should be rated for it.
    Mar 2009
    Eureka, CA
    3,900
    811
    1409
    240 volts at the button is considered lethal voltage and is verboten in many places...as I recall.
    Stuart
    Dec 2019
    NEW ZEALAND
    106
    23
    Might be a regional thing. A lot of simple control equipment here in NZ has 400V on the buttons.
    As long as the button is suitably rated for mains voltage and all wiring is contained in the box, there's nothing wrong with it - 277V light switches exist, too.
  7. Likes TDegenhart liked this post
    Apr 2018
    3,973
    1794
    Quote Originally Posted by SomeoneSomewhere View Post
    US is a little more safety-conscious. They don't run 220v to the vacuum cleaner, either
  9. #8
    Aug 2007
    GA
    802
    138
    normally if in the same cabinet I would run line voltage as control voltage but this application requires 24 vac