Trouble shooting three phase motor- where to start.
Results 1 to 5 of 5
    Oct 2010
    Maryland- USA
    5,157
    2490
    3201
    Default Trouble shooting three phase motor- where to start.
    I have a five hp three phase motor on a machine which won’t run.
    It surges briefly- like a 1/8 turn when I connect to power and makes a deep hum but won’t run.
    Where to start troubleshooting?
    The motor is spins perfectly free.
    Thanks all
    Jun 2001
    St Louis
    19,651
    2519
    3820
    Step one.... make sure all wires are carrying current. If not , proceed. If so, then there is another issue, possibly with the connection of coils.
    Step 2 make sure all 3 are properly connected
    Step 3 check resistance of all 3.
  3. Likes Lt. Swarf liked this post
    May 2013
    Germany, New Zealand.
    119
    27
    30
    Sounds like you have lost a phase. As above, check what is getting to the motor.
    Oct 2010
    Maryland- USA
    5,157
    2490
    3201
    Ok- I checked supply- all is good.
    This is a large belt sander and the 5 hp is the primary belt motor.
    The machine also has a three phase oscillating motor which works fine.
    Oct 2010
    Maryland- USA
    5,157
    2490
    3201
    You guys were right on it and that helped sort it out- the service disconnect for the main motor had punky contacts and were dropping a leg.