I wired up a few VFDs and I'm confused by the required wire gauge. I used a pair of Nidec (Control Techniques) Unidrive M300's, running on single-phase 110VAC. One is 1/3HP, the other 1.5HP. Per the manual, both of these required a 15A breaker.
With the wire ampacity tables from NFPA 79, I need 14ga from the breaker to the drive, and, because there's no circuit protection after the drive, I also have 14ga from the drive to the motor. If this were a direct-on-line motor, I would put a small breaker on the 1/3HP motor and be able to use much smaller wire.
If I go look at the manual, however, Nidec recommends 16ga on the input to the 1/3HP and 10ga on the input to the 1.5HP. They recommend 16ga on the output for both of them.
This problem would appear to be far worse if I'd used a different brand of VFD. The 1.5HP Delta drive wants a 50A breaker but has a maximum wire size of 14ga.
I'm trying to understand the correct way to wire these. In reality, the answer is that the gauges from the manual should be fine, but I would like to understand how to do an NFPA 79 compliant installation.