Wired rpc to 600 transformer.......... Issues
Results 1 to 12 of 12
    Dec 2006
    CANADA
    Ontario
    143
    11
    7
    Default Wired rpc to 600 transformer.......... Issues
    Hello Pm
    I have a Finch Williams rpc, built it myself and recently wired a 15 kva 240\600 transformer.
    The hook up seemed straight forward but perhaps I've over looked something. I wired T1, T2 & T3 from rpc to X1, X2 & X3 on the transformer.
    Any suggestions?
    Attached Thumbnails Attached Thumbnails 1445808368418.jpg   1445810056445.jpg   1445808429844.jpg   1445808322854.jpg
    Dec 2006
    CANADA
    Ontario
    143
    11
    7
    It buzzes and will not build rpms
    Jun 2001
    St Louis
    18,418
    2040
    3217
    So, what is the size of the RPC in kVA / HP?
    WHAT will not build rpms? The RPC? You do not want a load on the RPC until you have it started up. If you are trying to start it with that in place, it won't work. Connect the transformer after the RPC is going.
  4. Likes digger doug, TDegenhart liked this post
    Dec 2006
    CANADA
    Ontario
    143
    11
    7
    It's 10 HP. No machines are on during start up. My rpc has worked fine for years.
    Are you saying the transformer is drawing a big enough load to prevent the rpc from starting and closing a set of contacts after start up is the way to solve it?
    Dec 2003
    Washington
    4,862
    2403
    4417
    Start the RPC and allow to come up to speed . . .
    Wait 3 - 5 seconds
    Close contactor between RPC and transformer (240V) and allow RPC speed to stabilize
    Wait 1 second or more
    Close contactor to load (600V)
  7. Likes TDegenhart, CalG liked this post
  8. #6
    Mar 2011
    Geneva Illinois USA
    6,439
    2817
    2521
    A transformer is nothing more than a motor without a load. It draws magnetizing current just like a motor.
    Tom
  9. Likes windsormw liked this post
  10. #7
    Dec 2003
    Washington
    4,862
    2403
    4417
    I used a similar setup for several years before we moved into a building with a 400kVA 480V 3-phase service.
    We designed a 2 lane log bucking line with 4 positioning conveyors each at 50HP and were able to power this drive cabinet (200HP of drives) and spin motors to rated speed with a 5HP RPC feeding a 15kVA 240:480 transformer . . . we couldn't accelerate the motors very fast but we could run them all and test all of our software all from this dinky little 5HP RPC and transformer combo.
  11. Likes windsormw liked this post
  12. #8
    Dec 2006
    CANADA
    Ontario
    143
    11
    7
    thats exactly what I needed to know ,
    Thanks PM , I'll give it a shot as soon as i scare up some more parts .
    Scott
  13. #9
    Jun 2001
    St Louis
    18,418
    2040
    3217
    Good. Should work OK then.
    One serious issue is that the transformer, if not disconnected, is a load on the STARTING circuit..... And that may be most of the issue here. The start circuit may not be able to function with that transformer loading it un-necessarily.
  14. Likes TDegenhart liked this post
  15. #10
    Feb 2004
    peekskill, NY
    25,296
    5146
    Disconnect the starting circuit stuff.
    Start the idler with a pony motor, unloaded. Then energize the
    idler, then put the transformer online after the idler is up to
    speed and the output is stable.
    If the idler won't keep running after the pony motor is
    removed, somethings wrong with the idler.
    If the idler chokes and spins down when the transformer is
    put online, there's something wrong with the transformer setup.
  16. #11
    Jan 2010
    Dresden On. Canada
    602
    1391
    125
    Did you get this working ? I'm close and I have some parts. ---Trevor
  17. #12
    Sep 2013
    CANADA
    Prince Edward Island
    9
    Scott, I have a 15 hp RPC coupled to a 15 kVA 240:600v autotransformer to run a 10 hp 600v planer.
    As note above, I start the RPC in a no load configuration then close the fused disconnect to power up the transformer, and then start the planer. Works like a charm.
    Suspect that all you require is a disconnect between the RPC and transformer.
  18. Likes JST, t.jones liked this post