what if I wanted to get a an RPC, you think it would then be wise of me to utilize a 3 phase main breaker panel ( QO of course). I could just use a 1Phase double pole breaker for the RPC. My biggest 3 phase item now is 4HP so say a 6hp RPC. I know about not using the wild leg to run computers.
Do you need special QO single pole breakers if used in a 3phase panel?
No, you want 3-Pole "common trip" breakers for 3-Phase loads.
Do not try to "gang" 3 X 1-pole. Do not buy pre-pinned or clip-ganged ones. Get the proper unitary ones. You need very few, and they last a really, really long time.
Any single-phase should come off the panel connected to the mains, not off the RPC. Even though in theory your RPC or a Phase-Perfect can supply 1-P, leg-to-leg, an RPC, Phase-Perfect, (or VFD) output is floating Delta until you corner-ground it. That means not all three legs are the same with respect to ground.
Far worse, you do not OWN a proper "Neutral" to utilize for 120 VAC service and MUST NOT use ground for that.
Use a 240 VAC to 120 VAC, "control" transformer in the machine if you NEED 120 VAC (or 24 VAC, or. or. or..) not from the mains 1-P panel.
ELSE - as I am doing - feed the
entire output through a Delta-Wye transformer and re-derive a local neutral, output side, for "five wire" service outlets. Those are the 3 legs, a local Neutral, and Protective Earth AKA "ground".
All three legs are commercial-3-P power-good off the Phase-Perfects. Those off the RPC, the "generated leg" should still be identified and avoided for controls, relay/contactor & "magnetic starter" coils, DRO or CNC electronics, task lighting, coolant pumps, & such, isolation transformer notwithstanding.
One Delta-Wye already here, (EGS/Hevi-Duty 27 KVA) two more to go, and it looks as if I will have spent about $700 to $900 per-each, even with bargain-hunting, as the freight alone is running above $230 each.
FWIW-not-much, the loadcenters I use ARE rated for corner-grounded Delta. My personal preferences are not that tolerant. Hence the spend.
3CW